W wiigelec Member Location Red Desert May 23, 2012 #1 When installing pole mounted distribution air-gap switch (35kV) do you provide fused cutouts on line side or load side of switch, or does it matter?Thanks
When installing pole mounted distribution air-gap switch (35kV) do you provide fused cutouts on line side or load side of switch, or does it matter?Thanks
R rcwilson Senior Member Location Redmond, WA May 23, 2012 #2 Switch on line side allows fuse replacement with circuit de-energized. That should also provide easier hot stick access to the cutout.
Switch on line side allows fuse replacement with circuit de-energized. That should also provide easier hot stick access to the cutout.