Distribution panel for whse

Status
Not open for further replies.
Chris Simms said:
Looking for a distribution for 3phase 480 with 3 200 breakers for a warehouse I dont even know where to begin to look.
Chris

What size feeder is going to supply that panel?

What will be the available short circuit current available?

As far as where, any large supply house should have sales people (not the counter people) that know how to order what you need once you tell them what you want to do.
 
what I believe I was looking for is a 400 amp 3phase distribution panel with 3 seperate disconnects.
This is for a building that was a machine shop but the new owners only use as a whse now and they are adding a new additional whse. The main service has to be moved to the outside of the new whse and all feeders to be rerun. We were looking to reduce the amperage (currently 800 amps) to 400 amps and replacing the current disconnect. ( have to move it anyway).
The building is use only for whse with a small office section. I also need some type of temp to feed the 3phase panels for the office and some lighting that are currently in use because this is a operating whse and the new building will be just under the old point of attachment
Chris
 
Chris Simms said:
what I believe I was looking for is a 400 amp 3phase distribution panel with 3 seperate disconnects.
You have options. Either a 3R panel or a gutter with three fused (or breaker) disconnects hanging off it. Cost it out...
 