Need assistance & clarification for evaluating the SCCR of an ICP. Below are the flow of the circuit and the components SCCR/IR.
Main CB (50 CB(50kA) - PDB - SPD (200 kA) - Comb. Controller (50 kA) - TB's
Question 1: Can I use the main CB-IR for the PDB-SCCR? thought that the PDB is protected by the main CB, or should I use a default value of 10kA for the PDB-SCCR since the main CB and PDB are not listed?
Question 2: Should I include the TB's after the combination controller for SCCR evaluation of a control panel? Again, I was under the impression that the combination controllers are protecting the TB's, so I can exclude the TB on the evaluation.
I used PDB because this will be use for a group of motors with a typical sizes.