sahafi

Member
If I have three phases source of power and my load are two air conditions each one 10amp single phase. First one from phase A to C and second one from B to C. My question phase A and B have the same amount of current but how about phase C? Is it total?
Thanks
 
O

oliver100

Guest
Re: dividing load

The current in phase C can not be the sum of A & B.
 

jtester

Senior Member
Location
Las Cruces N.M.
Re: dividing load

The current in Phase C is the sum of A & B, however it isn't the algebraic sum, it is the vector sum. Phase C has 17.32 amps on it.
Jim T
 