DIY pictures of the day to learn from
ivsenroute
Florida
When I saw this setup on this 2 year old garage that was built without a permit, has no footing in an area that has a 42" frost depth with an undermined slab, I knew the sub panel inside would not be any better. Yeah, that is NM outside.
Would not expect anything less from inside the sub panel.
CopperTone
MetroWest, MA
so that panel is not actually grounded is it?
if you touched your testers one to the hot breaker and the other to the metal panel you wouldn't get a voltage reading. so if a hot wire came in contact with the panel it would energize the panel.
I had one like this 2 days ago. there was no bonding strap - good - but the grounds and neutrals were all on the same lifted bar. moved the grounds to a bar attached to the panel and wow same test and there is my voltage.
guess who installed it originally? the HO.
ivsenroute
Florida
50A breaker in the main feeds the 6/3 NM through PVC conduit to the sub so the 100A main is not a safety issue.
No Bond, no ground rods, just the NM from main to sub as you see it.
izak
Springfield, MO
did you check with a meter to see if the 'neutral' bus was bonded to case? the SQ D homeline main breaker panels ive run across have the 'neutral' bonded to case from factory and there isnt much way to seperate it from case and create a 4 wire system without violating SQ D specs
usually a main breaker resi panel doesnt include a ground bus because they are meant to be used as a 3 wire (service equipment)
LarryFine
Henrico County, VA
Electrical Contractor
Again, clearly the piocture shows the entire neutral bus assembly, and there's no enclosure bond.
I've never seen that. The EGC bus(es) may be inseparable, but the neutral bus(es), always are.
In fact, in the OP pic, the bottom-left bare wire appears to be the #10 from the NM feeder, which means it's in parellel with the feeder neutral, a no-no regardless of the code cycle (not) being followed at the time.
The simple fix, though non-compliant with the factory, is to cut the neutral jumper, insert the bonding screw, make the side with the screw into the EGC bus and the side without the screw into the neutral bus.
wireguru
or you could grab the $4 ground bar kit for that can :smile:
and on that note, man some of the homeline stuff is cheap at homedepot. I paid $39 the other day for a 12/24 indoor, ML convertible with 5 free 20a breakers
steelersman
Lake Ridge, VA
nothing's free. The panel simply came with 5-20 amp breakers that you paid for. :)
don_resqcapt19
Illinois
retired electrician
Larry, there are panels that are listed as "suitable only for service equipment". These panels have the neutral/grounding bus permanently connected to the enclosure. You cannot use these panels in applications where the neutral is not permitted to be bonded to the enclosure. Only panels listed as "suitable for use as service equipment" have the removable bond.