He said there are (6) sets of 444 kcmil RHH/RHW-2/DLO conductors that run from the XFMR secondary terminals, through a window cut out between the XFMR & SWBD, and to the SWBD main breaker. It is not a long jump to the conclusion that there are no special terminations on the transformer side or the SWBD side to avoid the use of Section 110.14(C)(1) which forces the reader to Table 310.15(B)(16).
Who said anything about avoiding the use of 110.14(C)(1)?
The problem is 110.14(C)(1) doesn't say what you think it says.