David,dnem said:And that couldn't have been done with 90? 2phase ?
The mathematical principals in Fortesque's Symetrical Components can be applied to any polyphase system of n phases where n is greater than 1, so, yes, one can analyze a two phase system with symetrical components.
The limited amount of long distance two phase transmission line is what says to me that there wasn't a lot of valuable transmission line and/or two phase generators that would get the development dollars to design, manufacture and install protective relays by the 1920s and 30s when the first applications of the math were occuring.
Before symetrical component math, a four wire, two phase generator without a common "neutral", would behave in understandable ways if the centertap of the windings were not connected together. The lack of the bond left the generator, essentially, as two separate single phase generators offset by 90? of rotation. The unbalanced or assymetrical conditions imposed on the two single phase parts of the generator could be understood by the mathematics of the late 1800s, and protection schemes for faults worked.