BuffaloBill
Member
- Location
- Buffalo, NY
- Occupation
- Electrical Project Engineer
There is a large VRLA battery (2700Ah) being installed in an industrial setting. It has a fault current value of ~32,000A. If the battery disconnect has an SCCR of 10,000, will it always need a current limiting fuse?
Also, assuming I use a current limiting fuse that brings the SCCR up to 200,000. Can I then use 10kAIC breakers in my panel if the battery is the only possible source of fault current? My thought is that since the fuse is designed to blow before the peak fault current is hit, then we should be able to have a lowered kAIC value in the downstream breakers.
Also, assuming I use a current limiting fuse that brings the SCCR up to 200,000. Can I then use 10kAIC breakers in my panel if the battery is the only possible source of fault current? My thought is that since the fuse is designed to blow before the peak fault current is hit, then we should be able to have a lowered kAIC value in the downstream breakers.