weressl
Esteemed Member
When I/we bring a building into compliance with 70E for arc flash labeling, all SE gear, panelboards, xfmrs, MCCs, and disconnects will be labeled. It's a pretty safe bet that by the time you're at a receptacle it's HRC 0, so no label's needed.
John M
Where you have 480V 3 phase receptacles throughout your plant feed from MCC's or panelboard it is entirely likely that they do have a higher than 0 HRC fault level available.