do i have to remove the old bonding to the water and steel if i install a new one?

Status
Not open for further replies.

dangerdale

New member
I am putting in a generator, the service is going to be changed along with the grounding. Do I have to remove the jumper around the water meter and to the steel if I install a new one?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I would say no. Parallel bonding and GEC's are permitted. The water meter jumper and CEE jumper is still required.
 

cadpoint

Senior Member
Location
Durham, NC
The service of the main will still require the main grounding and bonding of downline circuits.