qcroanoke
Sometimes I don't know if I'm the boxer or the bag
- Location
- Roanoke, VA.
- Occupation
- Sorta retired........
Have an installation where we have 120/208 3 phase service coming into the building. We also have a 200 kw genset with dual outputs 1- 400 amp output 1- 200 amp output.
Here's where it gets interesting. Generator output is 120/240 3 phase delta (high leg). 400 amp output will feed delta loads.
200 amp output will feed delta/wye transformer creating a SDS that will feed our loads through the ATS. We will most likely bond in the Xfmr. Thereby creating 2 bonded systems in the same ATS.
I'm pretty sure I already know the answer to this, but, do I need a 4 pole ATS to switch the neutrals to meet code?
Or is there an alternative to a 4 pole switch?
THANKS!
Here's where it gets interesting. Generator output is 120/240 3 phase delta (high leg). 400 amp output will feed delta loads.
200 amp output will feed delta/wye transformer creating a SDS that will feed our loads through the ATS. We will most likely bond in the Xfmr. Thereby creating 2 bonded systems in the same ATS.
I'm pretty sure I already know the answer to this, but, do I need a 4 pole ATS to switch the neutrals to meet code?
Or is there an alternative to a 4 pole switch?
THANKS!