Guys, my point to quoting 250.142 is a technical point.
I agree that the transformer is wired in Smart$'s drawing exactly like a non SDS generator and i agree we could call it a non seperately derived transformer.
Article 250.35 gives us permission to wire generators as non seperately derived systems. There is not a single article that gives us permission to wire transformers as non seperately derived systems.
Article 250.142 gives us permission to use the grounded conductor in the following manner...
A grounded circuit conductor shall be permitted to ground non?current-carrying metal parts of equipment, raceways, and other enclosures at any of the following locations:
(1) On the supply side or within the enclosure of the ac service-disconnecting means
(2) On the supply side or within the enclosure of the main disconnecting means for separate buildings as provided in 250.32(B)
(3) On the supply side or within the enclosure of the main disconnecting means or overcurrent devices of a separately derived system where permitted by 250.30(A)(1)
Since this transformer is not a SDS and it does not fit any of the 3 listed locations and is not a generator, the grounded conductor does not have permission to be used to "ground non?current-carrying metal parts of equipment, raceways, and other enclosures"
My technical point is untill permission is granted, this install is unsat.
Rick
RUWired I now understand your point and a very good point at that. As I said before....I have to study on this one.