8 Unit Apartment Building
Existing FPE equipment currently being considered for replacement due to known issues and proximity to the beach (salt air). No other know service related issues (decent condition)other than known FPE problens (though none apparent).
Existing Overhead service, 9 meters total - 8 units & a house. I will be performing no work on the line side of the meters. Only 2 CB's in existing pnls - 20/20 & 20. All pnls located in common dog house at rear of bldg.
No Ground Rod visable . Existing GEC to local H20 (hose bib), but connection is 75+ feet from H20 entrance. The GEC and Neut/Gnd Bond connections are located within a gutter above the meter sockets. This gutter also contains the line side taps to the 9 meter sockets. NO WORK HERE FOR ME - on the line side (???)
NO EGC.
Wiring method is EMT from meter to pnls.
The load side of the Discos' are RFMC (steel)
<<<<<PROPOSED SCOPE OF WORK>>>>>
Replace the existing FPE pnls with 70 Amp Square D (Homeline) equipment of the same physical size. The new equipment is sutable for Service Equipment if not more than 2 discos present. 20/20 & 20 = 2
Existing Mechanical Bond for EGC (no green wire). When the FPE equipment is upgraded to SQ-D, I will use grounding locknuts on the 1" EMT feeder conduits. 1/2 RFMC is GEC to the units.
<<<<<<<<QUESTIONS>>>>>>>>>>
Can I replace the pnls without opening up a can of worms on the GEC side. Would I be required to satisfy current NEC standards regarding the complete Grounding Electrode System if I go forward with the work.
<<<<Reason for Asking>>>>>>
If these pnls were inside the units I would consider them "subs" fed by service equipment because of the required OCD's. Do I have to consider them service equipment in this case. And if so, do I need to upgrade the H20 GEC and add a suplimental GEC (rod)
The funds do not permit a complete service upgrade and running a GEC to the proper location requires $$$$$ or surface mounting. Neither of which is acceptable to the owner of the building.
Existing FPE equipment currently being considered for replacement due to known issues and proximity to the beach (salt air). No other know service related issues (decent condition)other than known FPE problens (though none apparent).
Existing Overhead service, 9 meters total - 8 units & a house. I will be performing no work on the line side of the meters. Only 2 CB's in existing pnls - 20/20 & 20. All pnls located in common dog house at rear of bldg.
No Ground Rod visable . Existing GEC to local H20 (hose bib), but connection is 75+ feet from H20 entrance. The GEC and Neut/Gnd Bond connections are located within a gutter above the meter sockets. This gutter also contains the line side taps to the 9 meter sockets. NO WORK HERE FOR ME - on the line side (???)
NO EGC.
Wiring method is EMT from meter to pnls.
The load side of the Discos' are RFMC (steel)
<<<<<PROPOSED SCOPE OF WORK>>>>>
Replace the existing FPE pnls with 70 Amp Square D (Homeline) equipment of the same physical size. The new equipment is sutable for Service Equipment if not more than 2 discos present. 20/20 & 20 = 2
Existing Mechanical Bond for EGC (no green wire). When the FPE equipment is upgraded to SQ-D, I will use grounding locknuts on the 1" EMT feeder conduits. 1/2 RFMC is GEC to the units.
<<<<<<<<QUESTIONS>>>>>>>>>>
Can I replace the pnls without opening up a can of worms on the GEC side. Would I be required to satisfy current NEC standards regarding the complete Grounding Electrode System if I go forward with the work.
<<<<Reason for Asking>>>>>>
If these pnls were inside the units I would consider them "subs" fed by service equipment because of the required OCD's. Do I have to consider them service equipment in this case. And if so, do I need to upgrade the H20 GEC and add a suplimental GEC (rod)
The funds do not permit a complete service upgrade and running a GEC to the proper location requires $$$$$ or surface mounting. Neither of which is acceptable to the owner of the building.