do I need a subpanel in a garage

Status
Not open for further replies.
I have a detached garage and the boss wants a lighting circuit and a recpetacle circuit there will only be 3 receptacles 3 lights nothing else. I say we need a disconnect because there will be more than one circuit. The boss says no we don't any code reference
 

frizbeedog

Senior Member
Location
Oregon
ryandumas28 said:
I have a detached garage and the boss wants a lighting circuit and a recpetacle circuit there will only be 3 receptacles 3 lights nothing else. I say we need a disconnect because there will be more than one circuit. The boss says no we don't any code reference

225.31

Disconnect required

2008
 

frizbeedog

Senior Member
Location
Oregon
See also 225.30

2008

You may use a multiwire branch circuit for your two circuits without a panel.

Dicsconnect it with a two pole switch.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
frizbeedog said:
See also 225.30

2008

You may use a multiwire branch circuit for your two circuits without a panel.

Dicsconnect it with a two pole switch.
You must use a mwbc if you don't install a panel and have 2 circuits.
 

frizbeedog

Senior Member
Location
Oregon
ryandumas28 said:
I don't have my code book with me but I will make sure I look it up when I get home Thanks Ryan

Welcome to the Forum

.....I might be repeating someone so bear with me. :)

This place has strange acoustics.

If you don't believe me just listen to me play my guitar. Yikes.
 

cadpoint

Senior Member
Location
Durham, NC
I think the the one thing not talked about that its the BOSS, that needs this done!
And I think the one employee suggestion of the week, is it to start saying, "Well boss, When...?!" &/or "We ain't, left yet..."
 