Do I need an EGC?

Status
Not open for further replies.
Because it violates 250.24(A)(5) and 250.32.
Excellent references, that show bare neutrals can't touch messengers & raceways, or violate separation of EGC & Neutral (Grounded).

Now see photo's below. Left weather-head service drop, and Right weather-head feeder.

I believe this is Triplex with all insulated conductors, one is marked White (for neutral), and has bonded feeder-side EGC to messenger.

That braded steel messenger does not comply with Table 250.122 for EGC sizing, but it still works, and passed inspection.
 

Attachments

  • Triplex-1.jpg
    Triplex-1.jpg
    55.2 KB · Views: 21
  • Triplex-2.jpg
    Triplex-2.jpg
    37.7 KB · Views: 21
  • Triplex-2back.jpg
    Triplex-2back.jpg
    32.8 KB · Views: 22
Last edited:
They also drove 2 ground rods, barely 6ft apart.
 

Attachments

  • Triplex-Rods.jpg
    Triplex-Rods.jpg
    99 KB · Views: 4
Your boss is describing a peg ground. Edison caused some severe hazards doing this. You can only have one ground connection, one system bonding jumper, unless you create a separately derived system. And from there everything must be bonded. What you describe breaks the bonding, or adds a second system bonding jumper. Either way it’s a Code violation and a safety hazard since there is no low impedance path anymore back to the transformer neutral. So then no way to trip on ground fault,
 