Fred B
Senior Member
- Location
- Upstate, NY
- Occupation
- Electrician
I know POCO may not make any changes on there side and not our concern overall.There's been no mention of changing any wire, just changing the panel due to a bad bus bar. Wire from the service point to the panel clearly needs to be upgraded, POCO probably wouldn't change anything on their side.
But Post #12 he stated this:
Thus some assumption of wiring upgrade but again OP seems to be unclear as to the service point. Also if indeed an electrician installed a 200A on a #8 wire after the service point should have his license investigated. As a side note doubt a #8 would even be able to be landed on a 200A terminal that normal mfg. size would be min conductor size for the lug of a #6.I know the wires on the drop down pole were also changed by the electrician and the utility guy did something up there, too.