RossS
- Research Triangle, NC USA
- Electrical engineer
thermal data during the process would have been interestingWago Test
Your picture is missing the contact surface on the bottom side, which in both types is much larger. Your image is just showing the means to put pressure on that other contact surface.Holy freggin' hell. Now I understand you all's posts. I did not take into consideration the way I wrapped the wire around the screw. My bad. The point was to show surface contact and I was trying to do it fast to get back to some other stuff. Opps. Bunch of jokers. LOL All good.
Dang it. It's too late to edit it above.
I think the WAGO's have a better spring than the push in connections of a switch or receptacle device has and are better connection than the switches/receptacles give you.Stab type for sure; if by spring type you mean wire nuts, no, not looking for those. And I couldn't find engineering type drawings/diagrams of the different types of WAGOs. I assume the push-in are just like stab type, but I'm not sure about the lever type. Those look like they might have a whole lot more metal-to-metal contact area.
I did have an incident where a lever lock did not survive the fault current during a fault incident one time.I had an oops hooking up a .5 KVA transformer in my shop a few weeks ago.
24 volt secondary. I can verify that the insulation on the conductor smoked and not the lever lock connection.
Under normal usage I don't see an issue.
same here. Has gotten to where I just use these on nearly all light fixtures anymore.I like these for wiring up lighting especially if I'm up on ladder trying to hold the light up while making up the connection.
Also great for temp lights.
true, but so far I've had no more call backs maybe even less call backs than for failed twist on connections.You know that it's not a labor sating device, when you have to go back !
I trust wago style or push-in quick connects for any sort of small stranded to solid connection. I have never trusted wire nutting those, the fine strands on fixture wires don't hold up well to splicing.
Anything else I'm using linemans and a wire nut, where the wire nut is more for insulation as I've already fully spliced them prior to application.
I negated the bottom contact surface on both images on purpose. They are both just flat pads so it should be approx the same for each instance.Your picture is missing the contact surface on the bottom side, which in both types is much larger. Your image is just showing the means to put pressure on that other contact surface.
But the connection may depend entirely on this back surface with the screw or clip simply providing a holding/pressing force.I negated the bottom contact surface on both images on purpose. They are both just flat pads so it should be approx the same for each instance.
Important to keep in mind here, I'm not debating the new lever lock Wago style. I have no issues with the levers, just the flipper-spring type. No way the metallurgy of a spring clamp can remotely compare to the clamping and holding force of a screw. Anyway, I'm no expert at anything, just adding to the conversation.I believe the device style stab-in uses only two pinch points while the wire nut clamp style uses pressure against the conductor.
Plus heat weakens the springiness, which leads to more heat, and the effect snowballs over time.No way the metallurgy of a spring clamp can remotely compare to the clamping and holding force of a screw.
I am not talking about the lever style either.Important to keep in mind here, I'm not debating the new lever lock Wago style. I have no issues with the levers, just the flipper-spring type. No way the metallurgy of a spring clamp can remotely compare to the clamping and holding force of a screw. Anyway, I'm no expert at anything, just adding to the conversation.
True, but bus stabs have much more contact area than a cylindrical conductor.Spring clamp designs have been successfully used for more than a few decades, in most plug-in breakers.
Another valid point.Plus heat weakens the springiness, which leads to more heat, and the effect snowballs over time.
Having been a desk-jocky engineer for the last 27 years and counting, I haven't seen a lot of spring type connections since I'm not out in the field installing devices all day like you all are. We design DOD, flights, and ISS equipment and it's ring lugs and torqued screws all the way here so I can't speak to what all brands use them and the longevity. It just seems like a failure waiting to happen to me.I am not talking about the lever style either.
I remember, some 15 years ago, when I got my first Hoffman enclosure heater with push-in connections.
But the QO bus connection is made with a type of spring clamp. CH, tan handle, breakers also use a clamp that has what looks like a helper spring.I remember old tandem QO breakers with push-in terminals.
Each connection is designed for its purpose. It is totally possible to engineer clamps for limited wire sizes.True, but bus stabs have much more contact area than a cylindrical conductor.