lester.cape
Member
- Location
- Las Vegas
I am looking for some more information pertaining to Article 250.8 (A) (6). I have recently purchase the Grounding VS Bonding course offered through this website, and to my understanding a self tapping screw that engages a minimum of two threads is legal. If you do the math this article requires a thread forming machine screw (self tapper) with at least 18 threads per inch. This is about 2.2 threads engaged in the Box. The box I am refering to would be a four square J-box. On anoter note groundclips are not listed in 1 through 6 but actually fall under item 8 that says other listed means. Ground clips are listed therefore legal to use. My question is: Do items 1-6 have to be ul listed? or am I wrong about self tapping screws being thread forming? The way it reads to me is this: If you want to use a permitted method <U>not identified </U>in 1 through 6 then 7 and 8 says it has to be listed. If you reverse this sentance is it still correct? Could I say that if the device is not UL listed it must meet requirments 1 through 6? I have an AHJ telling me self tapping screws have to be listed and I am trying to figure out if this is correct.
Also does anyone know were the two thread engagement came from. Is it derived from a UL standard? Did somebody test a screw in a box and determine that two threads provides adequate continuty for a low impedance path back to the source?
Also does anyone know were the two thread engagement came from. Is it derived from a UL standard? Did somebody test a screw in a box and determine that two threads provides adequate continuty for a low impedance path back to the source?