Hello,
We recently ran power to some heat mats on a roof designed to take care of a ice build up issue on a flat roof.
We installed ground fault protection as per code. When the mats were turned on after awhile the ground fault protection tripped.
The ground fault is a separate unit and the circuit is not over loaded.
We took a megger and tested the mats and they all checked out just fine.
We then called the manufacturer and they told us that there mats do not need ground fault protection as it is not a resistive load.
They say it is a carbon nano sheet heating element (which I know nothing about) and it sends false readings and trips the ground fault protection.
Here is there sheet that they sent us and they say everything is UL listed after we asked them. Any input is greatly appreciated as we are hesitant of disconnecting the ground fault protection.
Thanks
We recently ran power to some heat mats on a roof designed to take care of a ice build up issue on a flat roof.
We installed ground fault protection as per code. When the mats were turned on after awhile the ground fault protection tripped.
The ground fault is a separate unit and the circuit is not over loaded.
We took a megger and tested the mats and they all checked out just fine.
We then called the manufacturer and they told us that there mats do not need ground fault protection as it is not a resistive load.
They say it is a carbon nano sheet heating element (which I know nothing about) and it sends false readings and trips the ground fault protection.
Here is there sheet that they sent us and they say everything is UL listed after we asked them. Any input is greatly appreciated as we are hesitant of disconnecting the ground fault protection.
Thanks