Re: do you run a grounding conducter from the meter to the p
lets think about this,,,,,what are we trying to acomplish by keeping the neutral and the grounds seperated???? we are eliminating parallel return paths,,,why? because where a ground wire is terminated on the neutral bar,this could impose neutral currents on the non current carrying parts of the electrical sysem.....or if the neutral was to become disconnected the neutral return currents would travel through the non current carrying parts of the system,,,,,including piping and ductwork,,if someone was to come in contact between the piping and a difference of potential ground a shock hazard would exist..or to provide a low impedence ground path to clear a fault...now lets say for some reason the neutral became disconnected in the main panel, where would the return neutral current try to go?IMO the neutral return current would still travel back to the main neutral bar,through the bonding screw in the main panel,throught the metallic parts between the main panel and the meter trying to get back to the neutral point at the meter wether a ground wire was installed between the meter and the main panel or not.In this case it is exactly opposite of a ground fault in the system which travels back on the ground wire,through the bonding screw,to the neutral bar and carried by the grounded conductor back to the source.I may be sticking my neck out here but with all that being said,if a ground wire is installed between the meter and the main panel is it not more than just an additional means of bonding the meter metal to the panel metal if it is at the service entrance?I know the ground wire is not large enough to carry fault current back to the meter like the neutral is but in an open neutral situation we would be relying on the interconnection of the metal parts only to clear the fault.I'm not talking about anywhere else other than the meter and main service disconnect location.