It is a typical residential meter bank(9' L in total), including a 1200amps MCB main service module(20"L) and 3 stacks of meters on one side and 4 stacks on the other side w/ 800 amps horizontal bus.
Do you guys think this meter bank is considered as large equipment (i.e. ratted 1200 amps or more and over 6' wide)? I think the point is that the meter bank is considered as one equipment or separate equipment (main service modules and two-meter stacks).
I am asking this because the electrical room only has one entrance and is not big enough. In this condition, if the meter bank is considered as large equipment, we need double the working space and ask the architect to enlarge the electrical room.

Do you guys think this meter bank is considered as large equipment (i.e. ratted 1200 amps or more and over 6' wide)? I think the point is that the meter bank is considered as one equipment or separate equipment (main service modules and two-meter stacks).
I am asking this because the electrical room only has one entrance and is not big enough. In this condition, if the meter bank is considered as large equipment, we need double the working space and ask the architect to enlarge the electrical room.