That's the way it reads to me.The title of the table mentions the length of steel conduit used as an equipment grounding conductor however the table mentions a wire equipment grounding
conductor. Are they trying to say the steel conduit is equivalent to the egc?
View attachment 2557678
That may also depend on the type of construction.Odd that nowhere on the table is steel conduit mentioned. Steel is supposed to have much less resistance than a copper wire used for the circuits in a particular conduit.
I also find it odd that there's no indication of how the conduit segments are joined. I would expect the couplers to have a significant influence on the overall impedance.... What I find odd is the size of the conduit isn't mentioned. ...
so, is this another 'study' by a manufacturer , of it's own product Don ?Take a look at figure 3 in this article. It gives the lengths of conduit that are acceptable for use as an EGC and the acceptable lengths of wire type equipment grounding conductors.
This information was developed by the Georgia Institute of Technology for the Steel Tube Institute. The Steel Tube Institute also has a free software program named GEMI to do these types of comparison calculations for equipment grounding paths.
It was sponsored by the steel tube institute, but the research is sound.so, is this another 'study' by a manufacturer , of it's own product Don ?
~RJ~
The documents were produced by Georgia Tech as contracted research project.so, is this another 'study' by a manufacturer , of it's own product Don ?
~RJ~
I agree. I think it makes a huge difference. Also, I would never use conduit as EGC simply because of the number of occasions I've seen EMT disconnected at a coupling.I also find it odd that there's no indication of how the conduit segments are joined. I would expect the couplers to have a significant influence on the overall impedance.
I agree. I think it makes a huge difference. Also, I would never use conduit as EGC simply because of the number of occasions I've seen EMT disconnected at a coupling.
Lol. Seriously, though, that could theoretically happen. Say a ground wire touches a neutral wire somewhere, that could potentially put a 120 volts on the load side of a disconnect conduit.Whereas I use EMT for the neutral whenever I can! (Tong firmly in cheek)
Steel is supposed to have much less resistance than a copper wire used for the circuits in a particular conduit.
Now I'm confused. Steel is well down the list of conductivity.
Silver
Copper
Gold
Aluminum
...
Steel
So I'm clearly missing your point.