quogueelectric
Senior Member
- Location
- new york
#3 is good for 100a past the service. They do not sell it in texas for obvious reasons.
quogueelectric said:#3 is good for 100a past the service. They do not sell it in texas for obvious reasons.
Texans think everything is bigger in Texas of course.buckofdurham said:What reason ?
Chamuit said:I've tried to get it here but no one I deal with carries #3 CU. It's either #4 or #2.
infinity said:We use #3 all of the time. Specifying #2 instead of #3 may lead to a need to up size the EGC
john_axelson said:You lost me, why does a change in wire size from #3 to #2 require a change in equipment grounding conductor? It has always been my understanding that the equipment grounding conductor is based on breaker size.
Did you mean the Grounding Electrode Conductor where the ground wire size is related to the Service-entrance conductor size?
We also use #3 all of the time.
Probably because someone finding upsized conductors may one day need to upsize the breaker feeding it, and the EGC might need to be changed, but probably wouldn't be.john_axelson said:You lost me, why does a change in wire size from #3 to #2 require a change in equipment grounding conductor?
LarryFine said:Probably because someone finding upsized conductors may one day need to upsize the breaker feeding it, and the EGC might need to be changed, but probably wouldn't be.
john_axelson said:I understand the concept and theory, but, a #8 EGC is good to 200A OCPD, I don't see the benefit of upsizing from a #8 to a #6 when pulling either #3 or #2, even if you did change the breaker size.
C3PO said:How is a #8 EGC good to 200A? It looks to me like it is good to 100A.