gaspower
Member
- Location
- United States
Aluminum floating dock. 20amp 120v service. GFCI on shore and on the dock.
Dock structure is bonded to ground wire from house load panel.
When swimming to aluminum ladder a strong tingle (uncomfortable) can be felt as you approach the ladder. Local EMC admitted it seemed odd but couldn’t figure it out. Almost all our neighbors had same issue, everyone had a ground rod installed on shore by a local electrician and issue went away (I measured a couple amps of current to ground rod on mine).
A few years later the tingle is back. Disconnecting the hot and neutral to the dock does not remove the tingle, but disconnecting the ground wire does.
Should I lean on EMC or call electrician back?
Dock structure is bonded to ground wire from house load panel.
When swimming to aluminum ladder a strong tingle (uncomfortable) can be felt as you approach the ladder. Local EMC admitted it seemed odd but couldn’t figure it out. Almost all our neighbors had same issue, everyone had a ground rod installed on shore by a local electrician and issue went away (I measured a couple amps of current to ground rod on mine).