Dock Service Demand Factors

Status
Not open for further replies.
We have a dock installation that we need some insite on.
After starting work on this private use dock for residential condos, the owner approached us with the notion of adding boat lifts for each slip of the dock. Utilizing a switch for isolation (only one lift per 2 slips able to operate at any given time) we only need to allow for 20 lifts in the calculation. After searching all through the NEC 2005 we cannot find any applicable demand factor for this installation. It is unrealistic that more than 2 lifts will be running at any given time once everything is complete. If anybody knows of any other possible demands we could use, we would appreciate your thoughts. As this was brought up after work was started, we have already installed a 200 A single phase service for this dock and the owner wants the lifts to be 120 V, dual 1/2 hp motor per lift.
 

beanland

Senior Member
Location
Vancouver, WA
Dock Demand

Dock Demand

This is a case where "engineering judgement" is needed. You need to size the service according to good engineering practices and work with the AHJ to their satisfaction.
 

bob

Senior Member
Location
Alabama
Dick Ziegler said:
we only need to allow for 20 lifts in the calculation. After searching all through the NEC 2005 we cannot find any applicable demand factor for this installation. It is unrealistic that more than 2 lifts will be running at any given time once everything is complete. If anybody knows of any other possible demands we could use, we would appreciate your thoughts. As this was brought up after work was started, we have already installed a 200 A single phase service for this dock and the owner wants the lifts to be 120 V, dual 1/2 hp motor per lift.
The NEC will not address a demand factor for this load. The load is only
20 1/2 hp motors and you have a 200 amp service, which is more that adequate. Is the other load the standard loads usually found at a site like this?
 
bob said:
The NEC will not address a demand factor for this load. The load is only
20 1/2 hp motors and you have a 200 amp service, which is more that adequate. Is the other load the standard loads usually found at a site like this?




The only other loads are 20 amp GFI outlets at each location.
 