Hello All,
My co-worker showed me his PV design like this:
The current goes out from a 300A AC output inverter to a 400AS/300AF fusible disconnect and then tap directly to the supply side of the main 600A breaker of a 600A main switchboard fed from POCO. The fusible disconnect is installed side by side with the 600A switchboard.
My argument is the switchboard is now overloaded 600A + 300A = 900A. So is a backfed PV breaker required and does 2014 NEC 705.12(D)(2)(3) apply in this case?
Thanks.
My co-worker showed me his PV design like this:
The current goes out from a 300A AC output inverter to a 400AS/300AF fusible disconnect and then tap directly to the supply side of the main 600A breaker of a 600A main switchboard fed from POCO. The fusible disconnect is installed side by side with the 600A switchboard.
My argument is the switchboard is now overloaded 600A + 300A = 900A. So is a backfed PV breaker required and does 2014 NEC 705.12(D)(2)(3) apply in this case?