I was wondering their is a 4" EMT that goes from a basement 100' then 90s up to 8th floor (over 80')to another 90 elbow and goes another 200' does 300.19 apply on the vertical run. Their are 4 600mcm and a ground in pipe
The conductors in the vertical portion would require support according to 300.19(A). Your 600 kcmil conductors will need support at the top of the vertical portion for every 40 vertical feet of raceway.