Hey guys, I've got a job at Rally's Hamburgers where I am to run a #8 ground from the main electrical panel to the data cabinet for a ground bar/surge suppression device they're installing. The only conductor I'm running is the ground wire from the top of the panel, above ceiling grid, to the data cabinet. Does the conductor need to be in conduit? TIA
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Unless this so somehow a GEC (which it isn't) I would say no protection required.
 

Rick 0920

Senior Member
Location
Jacksonville, FL
Occupation
Electrical Instructor
It would look better if it were concealed in conduit where exposed. Use PVC though. If you use metal conduit, you would need a bonding bushing for the conduit.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Doesn't this run afoul of NEC 300.3(B) - all conductors of the same circuit are to be run together in the same cable or raceway?
 

ron

Senior Member
If there area above the ceiling is used per 300.22(C) (environmental air), and you were running a green insulated conductor, then it would need to be in conduit. Regular building wire insulation is not plenum rated. Or you can run bare.
 