- Location
- Bremerton, Washington
- Occupation
- Master Electrician
One of my students installs furnaces. The newer types with electronic circuit boards require a "ground", however, I suspect what is required is an equipment grounding (bonding) conductor in the supply circuit. Apparently the furnace will lock out without a "ground", as is the case when a new furnace is installed on a 2 wire circuit in an existing house.
So, does an furnace electronics require a ground?,or is it just a misuse of the term ground and the furnace really requires an equipment gronding (bonding) conductor?
If thats the case, the correct solution would be a new branch circuit that contains an EGC to allow an installaion per NEC section 250.104
So, does an furnace electronics require a ground?,or is it just a misuse of the term ground and the furnace really requires an equipment gronding (bonding) conductor?
If thats the case, the correct solution would be a new branch circuit that contains an EGC to allow an installaion per NEC section 250.104