brycenesbitt
Senior Member
- Location
- United States
Does anyone still make a flush mount meter/main product?
We have a panel that's shot, that's flush mount, and there's really no room for a modern panel.
Working space rules won't permit a surface mount solution, and various constraints hamper moving the service.
Old panel
200 amps, rule of 6, six 50 amp breakers
38 inches high, 18 inches wide, 3.5 inches deep, flush mount between studs (the meters protrude from the wall)
Standard new panel quote:
I checked Eaton's B-Line, and did not do much better.
For the old panel:
There's no problem with capacity, but there's evidence of arcing, and one of the meter rings is not original,
having apparently been welded on from another meter main of a similar (but not identical) panel. Low income property, multiple units.
We have a panel that's shot, that's flush mount, and there's really no room for a modern panel.
Working space rules won't permit a surface mount solution, and various constraints hamper moving the service.
Old panel
200 amps, rule of 6, six 50 amp breakers
38 inches high, 18 inches wide, 3.5 inches deep, flush mount between studs (the meters protrude from the wall)
Standard new panel quote:
| Vendor | Part Number | quantity | Description | height | width | depth | Online Price | ||
| Siemens | WB1400C | 1 | unit | PowerMod 400A U/G service entrance 1-phase | 39.19 | 15.20 | 11.03 | inches | $ 2,506.00 |
| Siemens | WMMA31125 | 3 | unit | PowerMod 3 Stack, ring 125A/50A sockets | 43.31 | 48.66 | 8.09 | inches | $ 1,267.00 |
| Siemens | WMMA31125 | 3 | unit | PowerMod 3 Stack, ring 125A/50A sockets | 43.31 | 48.66 | 8.09 | inches | $ 1,267.00 |
| Siemens | WMT11225 | 1 | unit | EUSERC Test Bypass Facility Single | 40.50 | 21.50 | 9.00 | inches | $ 1,595.00 |
| Siemens | WMT11225 | 1 | unit | EUSERC Test Bypass Facility Single | 40.50 | 21.50 | 9.00 | inches | $ 1,595.00 |
| Siemens | WSPD3N20C | 1 | units | Low Voltage Surge Protection Through Bus | 29.19 | 13.38 | 7.75 | inches | $ 6,000.00 |
| 43.31 | 168.90 | 11.03 |
For the old panel:
There's no problem with capacity, but there's evidence of arcing, and one of the meter rings is not original,
having apparently been welded on from another meter main of a similar (but not identical) panel. Low income property, multiple units.