powersupplyguy@netzero.ne
- Warner, NH
Greetings,
I am building a machine which has a few 1kW LED drivers on board. The output voltage of these power supplies is 10v. The 10v travels down some SOOW cord to another enclosure with some LED lamps. The question is, do I need to ground the enclosure with the LED lamps in it?
Section 250.162 call out that a system over 50v must be grounded. There is an exception (#2)which further states that a rectifier-derived dc system supplied by an AC system complying with 250.20 shall not be required to be grounded.
Since my system is <50v and the voltage is a rectifier-derived (there is a high frequency transformer followed by a rectifier within the power supply) dc system, I expect I am not required to ground. Am I interpreting this correctly?
thank you
Bob
thank you
Bob