Hello All,
Had a meeting with the Utility planner yesterday. And presented the Main Panel Configuration that was created by EE. The Planner said that they would approve the project so long as the Main Disconnect complies with the Schematic [315 EUSERC. See ESR-3, Figure 3-10 (Displayed Below)]. I have lost me EE during this project and kind of been on my own. As you can see the attached Drawing, we are planning to install: Square D - EZM1400CBU - Main circuit breaker unit, EZ Meter-Pak, 400A, 120/240VAC, 1ph/3W, 400A bus, 100kA, UG, Type 3R.
Question: How can I tell if the Main Disconnect Square D - EZM1400CBU complies with the Schematic [315 EUSERC. See ESR-3, Figure 3-10 (Displayed Below)]?
Had a meeting with the Utility planner yesterday. And presented the Main Panel Configuration that was created by EE. The Planner said that they would approve the project so long as the Main Disconnect complies with the Schematic [315 EUSERC. See ESR-3, Figure 3-10 (Displayed Below)]. I have lost me EE during this project and kind of been on my own. As you can see the attached Drawing, we are planning to install: Square D - EZM1400CBU - Main circuit breaker unit, EZ Meter-Pak, 400A, 120/240VAC, 1ph/3W, 400A bus, 100kA, UG, Type 3R.