I don't see it in the load center catalog; just curious if anyone has ever seen a CH 20/1 breaker w/ bell alarm contacts? Would be the equivalent of Square D QO1202100 option.
@electrical/documents/content/pg74a01te.pdf
@electrical/documents/content/pg74a01te.pdf
some time back..
the server refuses to work with the link..
You could just put a relay across l-n on the breaker and use a nc contact as the alarm.
Some times we don't get what we want and have to take what we can get. Potentially you could replace the one pole breaker with a 2 pole breaker and use the second pole but the relay is simpler and cheaper.Yeh, I just preferred it be integrated into the breaker.
Sent from my iPhone using Tapatalk