If you run cables in EMT conduit, does this provide a 2 hour fire rating?
It amazes me how different each of us reads a question.
Thanks, I guess the reply with the 20 second rating answered my question. Just was curious about any type of cable in EMT. Same for RGS? Conduit does not give a rating to a cable right.
A requirement for fire alarm cable riser cable in NYC is to be 2 hour rated. I was trying to see if by putting the fire alarm cable in EMT, would the entire fire alarm cable considered 2 hour rated now this it is enclosed in conduit?
A requirement for fire alarm cable riser cable in NYC is to be 2 hour rated. I was trying to see if by putting the fire alarm cable in EMT, would the entire fire alarm cable considered 2 hour rated now this it is enclosed in conduit?
A requirement for fire alarm cable riser cable in NYC is to be 2 hour rated. I was trying to see if by putting the fire alarm cable in EMT, would the entire fire alarm cable considered 2 hour rated now this it is enclosed in conduit?
In of itself...NOPE.....Now elaborate in more detail. What type of cables are you placing in the EMT....and that may not even matter.If you run cables in EMT conduit, does this provide a 2 hour fire rating?