do you mean the risers are PVC also. You wrote underground twice.
ed downey said:Roger,
I have a question regarding this situation.
If the conductor is in PVC underground with GRC 90's on each end and PVC underground.
1.) Is this an acceptable installation?
ed downey said:2.) if it is acceptable do you need to bond the ends of the GRC that stub up through the poured slab? or should this be either all PVC or All GRC (or some other metal conduit)?
ed downey said:Just curious because I see this quite a bit on large projects that require (per the specifications) that GRC 90's be used to turn up through a slab.
Thanks,
Ed
GRC = RMC, but specifically stands for Galvanized Rigid ConduitFirmlyGrounded said:GRC?
The choke effect only occurs when a single conductor of an AC circuit it run through a magnetic raceway. The GEC is a single conductor of an AC circuit and to eliminate the choke effect problems, you must bond the GEC to both ends of every section of magnetic raceway. This same problem does not occur with EGC because the other conductors of the circuit are withing the same raceway. Of course, all metal parts of the electrical system are required to be bonded by the code rules, however in the case of conduits with an EGC and the circuit conductors this bonding is only required at one point, normally the supply end of the raceway.Why does it make any difference to electrons whether it's a EGC or GEC conduit when bonding?
don_resqcapt19 said:sparkie001,
The choke effect only occurs when a single conductor of an AC circuit it run through a magnetic raceway. Don
tom baker said:Don: I hadn't considered this issue with a EGC, however it would occur, thats why 300.5 requires all conductors in the same raceway, except for bonding jumpers, limited to 6 ft
But, functionally speaking, wouldn't the problem be more acute with a GEC due to the high (20,000 amps) current and higher lightning frequecy?
Whats interesting is the code recoginzes the problem for all circuits and picks the magic number of 6 ft. Probably this number is from the same proposal that set up 25 ohms for ground rod resistance. That documentation and reasoning is long gone.
don_resqcapt19 said:sparkie001,
you must bond the GEC to both ends of every section of magnetic raceway.
Don
You will find the answer on the first page of this thread.Luketrician said:Which is why it is a violation right?