kevinbur
Member
- Location
- United States
I was creating a spreadsheet to calculate conduit fill using the calculations given in Chapter 9 of the 2011 NEC and I think I may have found some incorrect values in table 5. After I finished my spreadsheet, I tried to back check the calculations with the values found in Table C.1 and it didn't work out correctly. I've taken into account the 0.8 remainder that will allow for one more conductor if all the conductors found in the conduit are of the same size and the different percent fill allowable per number of wires.
My issue seems to be with the conductor properties of THW/THHW #14 - 8 AWG conductors in Chapter 9 Table 5. Their properties match those of XHW/XHHW (same sizes); however, they do not have the same maximum number of conductors in EMT on Table C.1. My tables calculate all other values correctly except for these four THW/THHW wire sizes. Am I missing something in my calculations or do one of these tables need to change?
- Kevin
My issue seems to be with the conductor properties of THW/THHW #14 - 8 AWG conductors in Chapter 9 Table 5. Their properties match those of XHW/XHHW (same sizes); however, they do not have the same maximum number of conductors in EMT on Table C.1. My tables calculate all other values correctly except for these four THW/THHW wire sizes. Am I missing something in my calculations or do one of these tables need to change?