Does neutral counts as a current carrying conductor?

Status
Not open for further replies.

rknikko

Member
In New York City, (Wye circuits) does the neutral counts as a current carrying conductor? Does the NEC 2002, 310.15(B)(4)(a) apply to us in NYC? At the time when the job was filed, it was still in NEC 2002. Pls help!

[ February 15, 2006, 09:23 AM: Message edited by: rknikko ]
 
Re: Does neutral counts as a current carrying conductor?

NEC 310.15 (B)(4)(c)... where the major portion of the load consists of nonlinear loads... the neutral is counted as a current carrying-conductor
 
Re: Does neutral counts as a current carrying conductor?

Most of the time, most of the loads are linear. Unless you have a vast great number of computers, or fluorescent lights, or VFDs, or other fancy electronics, the loads are likely to be less than 50% non-linear.

But for us to answer your question, you would need to tell us what kind of power system you are talking about. For a single phase, 2-wire branch circuit, the neutral is always counted. For a single phase, multi-wire branch circuit,, the neutral is probably not counted. For a three phase, 4- wire branch circuit or feeder, the neutral is probably not counted. What are you working with?
 
Re: Does neutral counts as a current carrying conductor?

I think this is a canidate for a Frequently Asked Question.

Steve
 
Re: Does neutral counts as a current carrying conductor?

This is for 3-family residential house. The line coming in to the meters is a single phase 3-wire. (Red, Black & White) But I was told that in NYC, the utility has a Wye three phase 4-wire system. So, which one should we take into consideration? I'm confused!
 
Re: Does neutral counts as a current carrying conductor?

Originally posted by rknikko:
This is for 3-family residential house. The line coming in to the meters is a single phase 3-wire. (Red, Black & White) But I was told that in NYC, the utility has a Wye three phase 4-wire system. So, which one should we take into consideration? I'm confused!
Because the supply is three phase four wire and you are only using two phase conductors and a neutral you must count the neutral as a current carrying conductor.
 
Re: Does neutral counts as a current carrying conductor?

Originally posted by steve66: I think this is a canidate for a Frequently Asked Question.
GOod idea. I have been keeping a running list of possible additions to the FAQ topic. I just added this item to the list. Thanks, Steve.
 
Re: Does neutral counts as a current carrying conductor?

I agree with Bob. NYC is under the 2002 NEC with several amendments. I was wondering, shouldn't someone who is working on a 3 family house know what the supply voltage is?
 