Does Table 430.52 apply?
Ponchik
CA
Electronologist
Does table 430-52 apply to fastened in utilization equipment ( 2 sump pumps) the are plugged in to two separate duplex receptacle?
Thanks
Thanks
I don't see why it wouldn't.
I would point out that you are allowed to go up to the next size standard rating of an OCPD. For CB, the lowest standard size rating is 15 Amps. So if the receptacles are on a 15 A CB, you are fine.
If they are on a 20A circuit, you might have an issue if the FLC is < 8 Amps.
The two pumps are 8.7A each plugged in to two separate 15A rated duplex receptacles, circuit wiring is 12 CU, the OCPD is 30A.