If you literally mean a plenum, you cannot install cable tray within it. It is not a wiring method permitted in 300.22(B).I'm asking about cable tray in Plenum, is it without cover or with cover, in light of NEC 300.22
and what kind of cables can be used above this cables
Please advise
If you mean "Other Space Used for Environmental Air", such as above a suspended ceiling used for return air of an HVAC system.
For all of the years I have been working in High rises and such, the space above a suspended ceiling used for return air is the very definition of an air plenum.
It means that you can run these types of cables "exposed" in "other spaces". Other types of cables and conductors have to be run inside a metallic wiring system (metal conduit, metal wireway, etc.).in 300.22 C/1, Type MI cable, Type MC cable without an overall nonmetalic covering, Type AC cable or other factory assembled multiconductor control or power cable that is specifically listed for use within an air-handling space
what that mean in light of your above reply
regards
David points you to code text which states otherwise. The likely reason you [formerly] believed such is because "low voltage" cables run in this "other space" are likely required to be plenum rated.For all of the years I have been working in High rises and such, the space above a suspended ceiling used for return air is the very definition of an air plenum.
See the Fine Print Note in section 300.22(C).
Definitions will vary. They are all derived from this one..."Air Plenum: Any space used to convey air in a building, furnace, or structure. The space above a suspended ceiling is often used as an air plenum. " from http://www.mascordefficientliving.com/content/faq-glossary.asp
or this "
a space, usually above a ceiling or below a floor, that can serve as a receiving chamber for air that has been heated or cooled to be distributed to inhabited areas." from http://dictionary.reference.com/browse/plenum
Seems like the code is being redundant, however your reference certainly absolves you of any redundancy.
Webster's Revised Unabridged Dictionary (1913) said:Plenum
(n.)
That state in which every part of space is supposed to be full of matter; -- opposed to vacuum.
Merriam-Webster Collegiate Dictionary said:1 a : a space or all space every part of which is full of matter b : an air-filled space in a structure especially : one that receives air from a blower for distribution (as in a ventilation system)
Note that by these definitions, a plenum can only be on the positive pressure side of the system. Return air is on the negative pressure side.WordNet said:2. an enclosed space in which the air pressure is higher than outside
or this "
Article 100: Definitions
Plenum: A compartment or chamber to which one or more air ducts are connected and that forms part of the air distribution system.
The only definition that is relevant is this:
And since the ceiling space is a compartment and thec connection between the Air handler and the ceiling is duct, the ceiling space is used as a plenum in this case. The Code is redundant.