Say you have a corner grounded B phase system with a 2 pole breaker that has a line to ground fault on A phase. The fault is only being cleared by the A phase contacts which sees the full L-L voltage because in this system L-G = L-L voltage.I am still not understanding. Consider what Jaggedben said in post #8. Now that makes inuitive sense. I guess I am not seeing how a breaker would see any difference in a L-L fault on a corder grounded vs a L-L fault on a center grounded system.
But in a center grounded system the same condition has 1 pole of the breaker clearing the fault to ground on line A, but this time it only sees the L-G voltage and not the L-L one.