Sure there is, "workmanlike manner".No code article on ugly
Where in the NEC does it say you can not run N/M surface mount if it is installed corectly?NM cable surface mounted in a finished area
No, but that should be between the owner and the contractor, not the contractor and the inspector. This case, if it only involved the inspectors red tag, would never see a jury. The judge would issue a summary judgement ruling that the section is too vague to be legally enforced. If it is a civil case involving an incident, that would be different.Would you hire an electrician that performs this type of work?
Of course you can staple NM to a finished wall, although the installation in the picture would still fail for lack of supports and not following the surfaceOriginally posted by noxx:
You may not simply tack NM cable to a finished wall.
2002 NEC
334.15 Exposed Work.
In exposed work, except as provided in 300.11(A), the cable shall be installed as specified in 334.15(A) through (C).
(A) To Follow Surface.
The cable shall closely follow the surface of the building finish or of running boards.
A through C, not A OR...etc. This includes "(b) protection from physical damage." The cable shall be protected where necessary by conduit, emt, rnc, guard strips, surface metal, etc.2002 NEC
334.15 Exposed Work.
In exposed work, except as provided in 300.11(A), the cable shall be installed as specified in 334.15(A) through (C).
Ok, so here it's stated that these terms are enforceable by the mere fact that they exist in the NEC, other wise they cannot be there.The NEC Stryle Manual says "3.2.1 Unenforceable Terms. The NEC shall not contain references or requirements that are unenforceable or vague.
Talk about context, shall not be used by who? The writers of the NEC, a court, an inspector?The terms contained in Table 3.2.1 shall be reviewed in context, and, if the resulting requirement is unenforceable or vague, the term shall not be used."