But the point is, it is not intended to serve the countertop surface. Say it's a duplex receptacle and two under-cabinet luminaries are to be plugged into it. GFCI protection required or not?
If it is in the wall not in the cabinet at 16" above then it would clearly require GFCI protection as it can be reached by a kitchen appliance cord intended or not, and can be considered serving the counter top, lights plugged in or not, the code is kind of bland in 210.8 in the way it just says receptacles serving the counter top, the same goes for a bathroom we wouldn't argue that any receptacle in a bathroom is required to be GFCI protected if it is an installed receptacle no matter what it was installed for (not the one inside of a bath fan that is a part of the fan)
Heres another problem that could come up, there was an allowance for receptacle mounted on the bottom of the cabinets facing down to allow for designs where some do not want the receptacles visible to be included in the required receptacles for the countertop 2'/4' rule.
Here is a quote from the 2011 hand book on this:
The maximum permitted height (20 in.) for a receptacle
outlet serving a countertop is based on the standard dimension
measured from the countertop to the bottom of the cabinets
located above the countertop. This provision allows
multioutlet assemblies installed on the bottom of the upper
cabinets to be used as the required countertop receptacle
outlet(s).
So if the receptacle can be used also for the counter top is has to be GFCI protected even if it is cut into the cabinet but facing down, sure one could say that it is in the cabinet but the fact remains that the receptacle is accessible from the counter top if it is within 20" I would even say if any appliance cord could reach it which would be 24" but that is stretching it, that is why I said as you did that if it is inside of the cabinet it is no longer accessible from the counter top as the distance would be too long.
Myself I would look at it from a liability point of view, if a homeowner were to plug in a faulty appliance into a receptacle that could be accessible from the counter top, how would you defend yourself if they were electrocuted? refrigerator and other fixed in-place appliance receptacles are clear they don't need GFCI protection as well as receptacles located "inside" of cabinets as we both agree on, these you would have an out if it came to a court battle but not one facing down in the bottom of a cabinet.
We all know Joe homeowner will unplug a light, sump pump, or even a garage door opener, if they needed another outlet, it was this reason they removed the exception to garages and basements and even went as far as to even require a GDO receptacle to be GFCI protected, and yes I have seen extension cords run to the GDO outlet because there was only one outlet for the whole garage installed.