Exposed SE and SER is common here.SO Richmond Virginia doesn't have an ordinance against it? Okay,
Exposed SE and SER is common here.SO Richmond Virginia doesn't have an ordinance against it? Okay,
Beauty adds to the install cost.
I quoted the wrong code section it should be 338(B)4 which sends you to 334.30 and that would require listed straps but this is only in the 2017.Is a strap a fitting?
Exposed SE and SER is common here.
In Washington we see very little SE cable as its not allowed for service entrance. Where its used is from the panel to ranges and furnaces, wiring that is often inside the building.
I see no need for one, what would it accomplish in a hole bored after the wall is already there?No one mentioned the lack of a sleeve/chase on the penetration thru the brick wall? :jawdrop:
No one mentioned the lack of a sleeve/chase on the penetration thru the brick wall? :jawdrop:
The code does not specify, remember that the AHJ has to "approve" everything per 110.2.Fence staples are ok? As are bent nails?
I have installed conduit with epoxy glue with the approval of the AHJDuct tape? Super glue?![]()
I don't see any cable ties being used to secure and support the SE cable. Cable ties are the only type of support that 340.30 requires to be listed.I quoted the wrong code section it should be 338(B)4 which sends you to 334.30 and that would require listed straps but this is only in the 2017.
334.30 Securing and Supporting. Nonmetallic-sheathed cable shall be supported and secured by staples; cable ties listed and identified for securement and support; or straps, hangers, or
similar fittings designed and installed so as not to damage the cable, at intervals not exceeding 1.4 m (41∕2 ft) and within 300 mm (12 in.) of every cable entry into enclosures such as
outlet boxes, junction boxes, cabinets, or fittings. Flat cables shall not be stapled on edge.
Okay for single-feeder-service usePlus #2 AL on a 100 amp breaker...
Outside of any local amendments - NEC only requires protection where subject to physical damage. See 338.12(B)(1).Seems like I remember that the NEC calls for cables if ran surface mounted have to be a certain height off the floor / ground. I'm pretty sure this came up for MC cable. Not sure about SER cables. Plus #2 AL on a 100 amp breaker...
Exposed SE and SER is common here.