Does you area allow this type of work ? (See Pic)

Status
Not open for further replies.
Exposed SE and SER is common here.


That pic is Indiana,

It's not common at all in NC. I have seen it a few times. But I'm in the Triangle area. Even with the ice storms and hurricanes with electricians rushing to get services back up.

You still hardly ever see it. I've seen plenty of old metal 1 1/4 mast. I
remember all the PVCs and Metal weather heads selling out.

Even when they didn't go through the soffit they are metal. Now most use PVC , unless of course they're going through the soffit. I thought maybe it was a county ordinance.
 
That is 10 shades of ugly. I especially like the mix of 2 hole pvc and metal straps. Really gives it the "we forgot the straps but had some on the truck look."

For the record, no one over here uses exposed SE/R cable. It's all pipe and wire.
 
In Washington we see very little SE cable as its not allowed for service entrance. Where its used is from the panel to ranges and furnaces, wiring that is often inside the building.

Tom, how does that work? With respect to the OP photo that shows the Service Disconnect for each meter, included in the meter pack, isn't each cable a feeder? Doesn't the service entrance end at the service disconnect?

Posters are calling the cable in the photo "SE", but isn't it technically four-conductor SER?
 
I quoted the wrong code section it should be 338(B)4 which sends you to 334.30 and that would require listed straps but this is only in the 2017.
I don't see any cable ties being used to secure and support the SE cable. Cable ties are the only type of support that 340.30 requires to be listed.
334.30 Securing and Supporting. Nonmetallic-sheathed cable shall be supported and secured by staples; cable ties listed and identified for securement and support; or straps, hangers, or
similar fittings designed and installed so as not to damage the cable, at intervals not exceeding 1.4 m (41∕2 ft) and within 300 mm (12 in.) of every cable entry into enclosures such as
outlet boxes, junction boxes, cabinets, or fittings. Flat cables shall not be stapled on edge.
 
Seems like I remember that the NEC calls for cables if ran surface mounted have to be a certain height off the floor / ground. I'm pretty sure this came up for MC cable. Not sure about SER cables. Plus #2 AL on a 100 amp breaker...
 
Seems like I remember that the NEC calls for cables if ran surface mounted have to be a certain height off the floor / ground. I'm pretty sure this came up for MC cable. Not sure about SER cables. Plus #2 AL on a 100 amp breaker...
Outside of any local amendments - NEC only requires protection where subject to physical damage. See 338.12(B)(1).

2 AL is permitted on a 100 amp breaker for supplying a dwelling unit if it complies with rules in 310.15(B)(7).
 