If you've got a door between two electric rooms, how do you remedy the fact that it will open "in" to one of the two rooms?
Mike
Mike
Isn't that a requirement of NFPA 101 (or is it 100, or 110? I have a copy at my office desk, but not at home)?I have seen this once before, the local jurisdiction required the transfer switch and panels for the emergency lighting to be in a seperate room.
Isn't that a requirement of NFPA 101 (or is it 100, or 110? I have a copy at my office desk, but not at home)?
This is a bit tricky, and I am not sure I have it right. So someone please check me. I think that in the 2005 NEC, you only need the door to swing out when you have "large equipment," a term meaning rated at 1200 amps or more and containing overcurrent devices. In 2008, any door that is within 25 feet of the entrance to, or path of egress from, the required working clearance, must open outwards and have panic hardware.