Door Holde Releaser Emergency Control Function for Egress
Door Holde Releaser Emergency Control Function for Egress
I am pretty sure that the door holder circuit isn't a protected premise control function. The circuit that disconnects the door holder is. The door holder can be a 120 volt circuit. As far as I know, the open door is a desire and/or a courtesy, not a code requirement. If it was a code requirement then they would have to come up with some way to leave the door open during a fire.
Chapter 21 Emergency Control Functions and Interfaces
21.1 Application. The provisions of Chapter 21 shall cover the minimum requirements for the interconnection of emergency control functions to the fire alarm system and emergency communications systems in accordance with and 21.2.1 through 21.2.3 and 23.8.1.1
21.8 Door Release Service.
21.8.3 All door hold-open release and integral door release and closure devices used for release service shall be monitored for integrity in accordance with Section 21.2.
21.8.4 Magnetic door holders that allow doors to close upon loss of operating power shall not be required to have a secondary power source.
At least that is settled. The only thing that make it a Protected Premises is the listing of the FA Unit or the permit presently issued to the owner. If door holders are added then the OP has to figure everything else corresponding to his post in the beginning of this thread.