do you need the door to swing out of an electrical room. (12' x 20') room has 480 and 208 volt power.
is that 1200 amps total in more than 1 piece of gear
Yes it is. Earlier versions talked about doors that comprise entrances to the working space. Only in 2008 did it include any door within 25 feet of the working space.is the less than 25ft rule new to 2008?
Here we do not require a door, but if it has one it will swing in the direction of egress. I cannot require panic hardware, but I can ask for it.
The IBC also has a requirement for panic hardware on some electrical room doors, although I forget the exact specifics.
I assume the IBC isn't adopted in your area?
Steve
It is and it reads the same as the NEC.
We don't seem to be on the same page. I was refering to your comment where you said you could not require panic hardware.
The IBC requires panic hardware in some cases. The NEC does not.
do you need the door to swing out of an electrical room. (12' x 20') room has 480 and 208 volt power.
Steve, I just reread you comment and you may be correct "......panic bars, pressure plates or other devices that are normally latched but open under simple pressure" is what the NEC says. Panic bars per say are not "required", but can be used. Where the IBC says "panic bars", but a panic bar is simply a "crash bar" and does not have to be alarmed. So while the wording is different, I believe that they are saying the same thing.
But again only under the conditions stated are they required.
Cowboy:
I think you are correct, it can be a crash bar, and it doesn't have to be alarmed.
However, the NEC allows a simple lever type door knob. The IBC (somewhere in paragraph 1008) requires panic hardware to extend at least half way across the door. So a simple lever type knob wouldn't satisfy the IBC requirements.
So if there is a door, and the room has 1200 amp equipment 6' wide, you can require a panic bar.