aelectricalman
Senior Member
- Location
- KY
I went to a home where I recently performed a rewire. After hooking up the range we noticed the burners were not heating up properly. You could lay your hand on the burners while on high. Anyhow, when we checked the voltage on the receptacle we measured 92V - L1 and 156V - L2. This circuit was a three wire with no neutral, so measurments are to ground. Ok, we first tested the system without the range turned on and we still had the same problem. We then checked the main and lo and beho it to read 92 and 156 respectively. So, one at a time we cut off every breaker until we came across a doorbell transformer that was hooked to a 20 amp single pole breaker. When we cut off the breaker servicing the doorbell, the load balanced out a 118v and 119v respectively. The doorbell transformer was hooked up correctly and appeared to be in good working order but there was something going on in the transformer that I cant figure out. I could see if the transformer was hooked up backward there being problems but what if there was a loose neutral on the transformer, could it cause such a swing. Can anyone produce documentation of this in such a small scale as a 120 to 24V step down xfmr. That is an awful big swing, I think?