Re: Doorbell Transformer in Panel
The real problem I see with installing these transformers inside of boxes is with 300.3(C)(1) which reads as follows:
"600 Volts, Nominal, or Less. Conductors of circuits rated 600 volts, nominal, or less, ac circuits, and dc circuits shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway."
As stated here the real problem lies with the insulation of the class II wire which is not rated for the voltage in the panel or even the box located behind the door chime. As I see it, these are code violations. I support the idea of installing a separate box for the purpose of properly mounting the door chime transformer in an area like a furnace room. If the room is finished, us a blank cover with a 1/2" KO.
Dirk