Doorway Class 1 Div 1

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Waiting on the engineering drawings but trying to head off a problem. Paint mix area, Class 1, with an overhead rollup door. The motor and contrils are outside the room itself. Is there normally a "halo" around door openings in Class 1 or is that specific to paint booths, etc.
 
Waiting on the engineering drawings but trying to head off a problem. Paint mix area, Class 1, with an overhead rollup door. The motor and contrils are outside the room itself. Is there normally a "halo" around door openings in Class 1 or is that specific to paint booths, etc.
Mixing alone does not usually introduce a classified location. Then again, "Class 1" only applies to Article 725; paint spray booths are usually Class I;). (Sorry Augie, I had to do it to someone.)
 
No problem.. In this case I'm just the messenger and thats the way it was presented to me :D
I may continue to put foot in mouth but you are already aware that Hazardous is a weak area for me so...
Generally speaking, other than Art 516, would you expect the area around the door to a classified area to be classified also, or is that too broad a question ?
 
Situations vary a lot, making any generalization hazardous (ha - pun).

Generally speaking, and based solely on NFPA 497 guidance (without a lot of thinking), I would say:

- If there is a Div 1 inside the door, and the door is opened as part of any expected activity (no matter how infrequent), the outside would also be Div 1;

- If there is a Div 1 inside the door, and the door is not opened as part of any expected activity (no matter how infrequent), but can be opened, the outside would be Div 2;

- If there is a Div 2 inside the door, and the door is opened as part of any expected activity (no matter how infrequent), the outside would also be Div 2;

- If there is a Div 2 inside the door, and the door is not opened as part of any expected activity, but can be opened, the outside is still Div 2.

Obviously situations vary a great deal, but a rule of thumb would be a Div 1 hazloc would extend outside the door to a 3'-5' radius in all directions; Div 2 might be up to 15' all directions.

I'm not saying that the paint mixing operation would actually give rise to any hazloc, but if it did, the above would be a reasonable first approximation.
 