T Toros Senior Member Location Tujunga, CA Jan 14, 2016 #1 Hi I have to determine the feeder sizes for verious, almost new molding equippments . in a iron molding factory attached is the list of equipm & thier feeders I prepared. Do you think this determination/ sizes are correct ???? Tanx Attachments Equipm. list +feeder size - MH.pdf 72.3 KB · Views: 0
Hi I have to determine the feeder sizes for verious, almost new molding equippments . in a iron molding factory attached is the list of equipm & thier feeders I prepared. Do you think this determination/ sizes are correct ???? Tanx
J jeremy.zinkofsky Senior Member Location nj Jan 14, 2016 #2 Just make sure that you are adhering to NEC Article 430.22(A) for your conductor selection amapacity.
Just make sure that you are adhering to NEC Article 430.22(A) for your conductor selection amapacity.
J jeremy.zinkofsky Senior Member Location nj Jan 14, 2016 #3 Not sure if you are choosing the overcurrent protection or not but if so, follow NEC Article 430.52 (C1)
Not sure if you are choosing the overcurrent protection or not but if so, follow NEC Article 430.52 (C1)
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jan 14, 2016 #4 Two factors to consider: (a) Does any of the equipment have nameplate or manufacturers info on overcurrent protection (b) Are there motors involved. I so, as mentioned above, you need to take 420.22 into account.
Two factors to consider: (a) Does any of the equipment have nameplate or manufacturers info on overcurrent protection (b) Are there motors involved. I so, as mentioned above, you need to take 420.22 into account.